[nut-Bugs][312364] Improvements for netvision mips (snmp-ups)
nut-bugs at alioth.debian.org
nut-bugs at alioth.debian.org
Tue Feb 23 17:06:36 UTC 2010
Bugs item #312364, was opened at 23/02/2010 17:06 by Andrea Soster
You can respond by visiting:
https://alioth.debian.org/tracker/?func=detail&atid=411542&aid=312364&group_id=30602
Status: Open
Priority: 3
Submitted By: Andrea Soster (sghebuz-guest)
Assigned to: Nobody (None)
Summary: Improvements for netvision mips (snmp-ups)
Category: Driver
Group: None
Resolution: None
Initial Comment:
Dear,
I'm testing a new ups (Sicom/Socomec MASTERSYS BC 15 KVA), and it works
with nut 2.4.1
After upgrading to 2.4.2/3 it's not working anymore: it's unable to see
the status.
I fixed the driver making it work again with 2.4.3 and made some
improvements:
1. The order of "netvision_output_info" is incorrect: fields with
null value come before the "OL" one, excluding it from the
lookup. For that reason nut was returning a blank status (and
upsmon wasn't very happy)
2. NETVISION_OID_BATTERYSTATUS was checked for
"netvision_batt_info" and "netvision_output_info". Now
"netvision_output_info" is checked on
NETVISION_OID_OUTPUT_SOURCE
3. If you start the shutdown procedure on the UPS, nut is not
receiving anything (as the ups is still online) -> Now it checks
alarm 50 - "UPS imminent stop" and send a FSD signal when
present
best regards
Andrea Soster
----------------------------------------------------------------------